Lights that dip every time the air conditioner kicks on. A chandelier that flutters like a candle when the dishwasher starts. A bedroom lamp that pulses late at night for no clear reason. I’ve seen all of those in Houston homes across every neighborhood, from older Montrose bungalows with patchwork additions to newer builds out past Cypress with long service runs and thirsty HVAC systems. Dimming and flicker feel like a nuisance, but they also point to specific stress points in a home’s electrical system. If you follow the signs, you can often trace the problem to a handful of repeat offenders and fix it for good.
I handle residential electrical repair across the city, and most calls about flicker land in one of three buckets: normal voltage dips from heavy loads, loose or failing connections, or oversensitive LED drivers and dimmers. Sometimes the culprit is smaller, like a worn lamp cord. Sometimes it’s bigger, like a service lateral with corroded splices that belongs to the utility. The trick is to sort symptoms with a structured approach, then choose the simplest reliable fix. Houston’s heat, humidity, and storm seasons shape the way we test and repair. What works in Phoenix does not map cleanly to a Gulf Coast climate. Moisture intrusion, thermal expansion, and salt-laden air change the story.
Lights dimming slightly for a second when a large motor starts, such as a 4 or 5 ton AC compressor, can be acceptable. Motors draw 3 to 6 times their running current at startup. On a typical 200 amp service, a brief sag that you can notice but that doesn’t make electronics reboot can be within bounds. Continuous flicker, repeated fluttering independent of big loads, or dimming that varies across rooms signals a problem worth chasing. If the dip is so deep that a microwave resets or a UPS clicks to battery, you’re outside the comfort zone.
The human eye notices changes in brightness more than it reads a voltmeter. Two homes can both dip from 121 volts to 116 volts and feel different based on the type of lamps installed. LED drivers react quickly to voltage changes and, in some designs, exaggerate the effect. Incandescent lamps smooth short blips because the filament holds heat for a beat. When assessing a complaint, I always ask what type of bulbs are installed and whether dimmers are in play.
The climate here speeds up aging. Summer attic temperatures hover north of 130 degrees. That heat cycles conductors, terminals, and breakers day after day. Outdoor meter cans bake in the afternoon sun then get drenched in evening storms. Underground service laterals wick moisture from our expansive clay soil. Add hurricane seasons that loosen mast heads and pull on service drops, and you get a recipe for loose or corroded connections. The stakes are real. Loose terminations create resistance, resistance makes heat, heat accelerates loosening, and then you get arcing, charred insulation, or nuisance trips.
Neighborhood infrastructure matters as well. Many parts of Houston have long secondary runs from transformers. If several houses on a transformer kick on high-SEER, variable-speed HVAC units around the same time, voltage sags ripple. Sometimes the fix starts with the utility because the issue sits upstream of the meter.
When lights dim, the first questions I ask cut the field in half. Do all lights dim, or only certain rooms? Do they dim when a particular appliance starts? Does the flicker happen across both legs of the panel, or mostly on one side? Is there any buzzing at the electrical panel or a warm breaker face? Has anyone added new LED bulbs or smart switches recently?
There is a rhythm to residential electrical repair. You want to rule out the easy, low-risk causes before you open walls or schedule a service mast rebuild. I rely on a mix of observation, portable monitoring, and simple voltage tests at strategic points, because the symptom can vanish the moment I remove a faceplate. The diagnostic setup often includes a voltage logger clipped to a nearby receptacle and, when appropriate, a clamp meter watching inrush current at the AC disconnect.
Loose neutrals at the panel or meter base sit at the top. When the shared neutral connection loosens in a split-phase system, loads on one leg can steal from the other, lights brighten on one side while others dim. It can look chaotic but aligns with math. In Houston, I see this in homes built in the 70s and 80s with aluminum service conductors, though copper isn’t immune. Sometimes the loose point is in the weatherhead or the utility’s tap splice inside the meter can. A neutral problem demands prompt attention. It can fry electronics and cook motors.
Second place goes to dimmer and LED driver incompatibility. Not all “dimmable” LEDs dim the same way. Many older or inexpensive LEDs require trailing-edge dimmers, while a legacy dimmer installed for incandescents works as a leading-edge device. The mismatch causes flicker at mid-range settings or shimmer around every little voltage change. If flicker only occurs on dimmed circuits and disappears when switches are set to full bright, I suspect this interaction.
Third, motor inrush paired with undersized or long branch circuits. A garage freezer on a 50-foot 14 gauge run can dim lights on the same circuit when the compressor kicks in. I’ve seen laundry rooms fed with 15 amp circuits shared with lighting, then a modern front-load washer strains the line. The fix often involves moving loads to dedicated circuits or upsizing wiring during other renovations.
Fourth, poorly made wirenut splices in lighting junction boxes. Heat in attics loosens older connections with brittle insulation. I have opened boxes where the copper barely touched and the wirenut held a pocket of air. A slight bump of the ladder would make the chandelier steady, then flicker again as the attic cooled that night. The repair feels simple, but it takes an hour of careful inspection to find each suspect joint, retwist, and torque caps properly.
Fifth, failing breakers or bus stabs in the electrical panel. Some older panels develop hot spots where breakers no longer bite firmly. If I remove a breaker and see burn marks or a discolored bus finger, the conversation turns to electrical panel repair or replacement. Houston humidity and occasional condensation inside garages accelerate this wear. A homeowner might notice a light pulsate when they shut a door and the panel vibrates slightly.
A few honorable mentions show up just often enough to keep me humble. Loose lampholder springs inside recessed can lights, especially retrofitted with LED trims, can make intermittent contact. Ceiling fan kits with cheap remote receivers introduce flicker as they fail. And then there are smart bulbs interacting with three-way circuits wired with old travelers that leak enough current to confuse the electronics.
Please keep safety in mind. If you see or smell burning, hear sizzling at the panel, or notice lights brightening and dimming at the same time in different rooms, cut power and call for professional help. For milder symptoms, a few careful steps can narrow the field.
These observations help us decide whether to focus on home electrical repair at switch legs and fixtures or start at the service equipment and work outward.
A careful inspection comes first. I look at the service mast, meter base, bonding, and the main panel. Any corrosion streaks under the meter, rusted screws, or gaps in mast flashing get attention. Inside the panel, I check torque on lugs with a calibrated wrench, scan for discoloration, and measure voltage on both legs under different loads. A voltage logger runs for a minimum of 24 hours if the issue is intermittent. In one Heights home, the chart told the story: every night around 9 p.m., voltage on one leg sagged 5 to 7 volts when four houses on the transformer ramped up variable-speed condensers. That sent me to the utility with data rather than guesses.
Branch circuit testing usually follows. If flicker is tied to a specific room, I’ll open the first device in the chain and the switch box, inspect splices, and confirm whether the circuit is daisy-chained through back-stabbed receptacles. Back-stab connections tend to loosen with heat and time. I move them to screw terminals and rework splices with fresh caps. Where neuter bundles exist, I verify that the neutrals are continuous and properly tied. A single loose pigtail can make half the lights on a circuit act haunted.
Dimmers and fixtures come next. I check model numbers against manufacturer compatibility charts. The better manufacturers publish tested pairings of dimmers and lamps. If a homeowner wants silent low-level dimming on kitchen pendants, I steer them to a matched set. It costs a little more than a grab-bag of sale-bin bulbs, but it works reliably. I also measure leakage current on smart switches. Some need a neutral to avoid trickle-draining through the lamp, which can create tiny pulses that read as flicker.
When the data points to service-side issues, we discuss electrical panel repair or upgrading feeders. If lugs are pitted or the bus is heat-damaged, I will not leave it as-is. I’d rather plan a short outage and rebuild correctly than nurse a system that overheats every August. If the problem likely sits at the utility connection, I document voltages and events and coordinate with the power company to check the transformer taps and the neutral connection at the pole or pedestal. In Houston, the utilities generally respond quickly when you present clear evidence.
Not every solution is glamorous. Often the cure is a combination of small improvements that together remove enough slop from the system to make lights steady again.
On older homes with aluminum service conductors, I clean and apply antioxidant compound, then torque lugs to spec, sometimes replacing lugs if they no longer hold well. If the meter base shows corrosion, I recommend replacement. A fresh, tight path from the service drop through the meter to the main breaker makes a large difference in voltage stability under load.
For panels with aged breakers and a pitted bus, we discuss replacement. Homeowners sometimes balk at the cost, but compare it to replacing multiple electronics over a few summers or risking a failure on a holiday weekend. Newer panels also give room to split overloaded circuits that were bundled together in the past. A remodel might have stacked kitchen lighting, undercabinet LEDs, and a microwave on a single 15 amp line. That saves wire but creates dimming headaches every dinner rush.
I often install soft-start kits on older AC compressors when startup dips are aggressive. Modern HVAC equipment often includes soft-start or variable-speed tech, but many existing systems present heavy inrush. A properly selected soft-start module reduces the voltage dip across the home at every cycle. Pair that with dedicated circuits for laundry and garage refrigerators, and the common “the lights blink when I run the washer” complaint disappears.
Upgrading dimmers solves a surprising number of cases. The newer ELV or adaptive-phase dimmers play nicely with quality LED lamps down to low levels without shimmer. The key is to choose a dimmer with enough wattage headroom, even though LEDs draw less power, because the electronics inside still generate heat in tight boxes. In kitchens with multi-gang boxes, I derate dimmers and plan box fill carefully to keep heat manageable in August.
Finally, rewiring long, skinny lighting runs improves voltage drop. In a two-story with the panel on one side of the house, lights on the far side may share a wiry path through multiple junctions. When feasible, we pull a new homerun in heavier gauge wire. The homeowner might not see the wire, but they notice steady light across the whole dimming range.
Every profession has cases that keep you honest. A Memorial-area home had periodic flicker that only happened at 3 a.m. and only in the nursery. We swapped lamps, tried new dimmers, and logged voltage without catching anything extraordinary. It turned out a whole-house surge protector installed by another contractor had a loose neutral lug. The device only clamped and made itself noticed when CenterPoint performed scheduled switching at night. Tightening and reterminating solved it.
Another job in Spring Branch involved a Tesla charger sharing a subpanel with lighting circuits. Every time charging ramped up, the dining room pendants twitched. The load calculation looked fine on paper, but the feeder to the subpanel ran undersized for the distance. We upgraded the feeder and rebalanced the panel, and the lights stopped dancing. Vehicles can act like big variable loads that change the rhythm of a house if conductors are marginal.
I also recall a Bellaire addition with designer fixtures that only flickered when the backyard pool pump started. We suspected voltage drop along the way, but the real gremlin was a chipped breaker with loose internal contacts feeding the pool subpanel. The pump worked, but the oscillation bled into the house and set off the sensitive LED drivers. Replacing the breaker and landing on a fresh bus position fixed it immediately.
Electricity does not forgive guesswork. If you suspect a loose neutral at the service, do not open the panel cover yourself. Even with the main off, service conductors and lugs remain energized. If you smell something metallic or see soot around a breaker, that is not a cosmetic issue. Cut power and call a licensed electrician. With LED flicker at mid-dim levels and no other symptoms, you can experiment with dimmer swaps and lamp replacements. But any symptom that affects multiple rooms, especially when appliances start, crosses from annoyance into risk.
GFCI and AFCI protections matter. I still find lighting circuits without proper arc-fault protection in older remodels. Nuisance tripping is often blamed, but a modern combination AFCI breaker reduces the chance that a loose connection becomes a smoldering problem. If your panel uses legacy breakers, ask about upgrading critical circuits during the next service call.
Surge protection deserves a brief word. Whole-house surge devices will not stop voltage sags, but they do protect electronics from spikes, especially in storms. I install them as part of an electrical panel repair or replacement because they are cheap insurance in lightning-prone regions.
A qualified pro should start with questions, not a sales pitch. Expect them to listen for patterns, then inspect the service equipment, panel, and representative fixtures. If the issue is intermittent, ask for a short-term monitoring plan. A good contractor will bring a voltage logger rather than guess. If they recommend electrical wiring repair inside junction boxes, they should explain what they saw, not just claim “bad wiring.”
In terms of timing, many residential electrical repair jobs for dimming and flicker wrap in a single visit, especially those involving dimmer replacements, fixture rewiring, or tightening and reterminating panel conductors. If the scope expands to electrical panel repair, soft-start installation, or meter base replacement, plan for a half-day to a full day. Coordination with the utility for service-side neutral issues can add a few days, but the visit itself is usually short once scheduled.
As for cost, simple fixes like swapping dimmers and correcting splices sit at the low end. A panel rebuild or service mast repair costs more but tends to pay back in reliability, fewer nuisance issues, and stronger resale narratives. Buyers in Houston increasingly ask for documentation of electrical upgrades, especially after major storms. A clean, modern panel with labeled circuits and visible surge protection makes a strong first impression.
For LEDs, stick to reputable brands and check compatibility charts. Many manufacturers publish specific pairings that guarantee smooth dimming. Avoid mixing bulb brands on the same dimmer. If you love very low-level ambience for dining or nursery rooms, choose LEDs designed for deep dimming and pair them with an ELV or adaptive-phase dimmer rated for LED loads.
For breakers and panels, consistency helps. Mixing old and new parts across different brands can create fit issues that lead to poor bus contact. If your home still uses a panel model with a known history of failures, talk about a planned replacement rather than waiting for a failure in August heat.
HVAC interactions deserve attention. If your AC causes noticeable dips, ask your HVAC contractor about soft-start options or confirm that the system’s factory electronics are active and configured. Pair that with ensuring the AC is on a correctly sized, dedicated circuit with a solid disconnect and tight lugs.
Sometimes, the house is fine. If both legs at the main panel sag together based on neighborhood demand, or if one leg floats high while the other falls, the issue may be at the transformer or the neutral path back to the utility. In Houston, utilities respond to documented voltage fluctuation complaints. A simple log showing events tied to times, plus panel measurements, gets traction. I have walked plenty of jobs where the fix was a new crimp at the pole or a tightened neutral in a pedestal cabinet after flood exposure. When we present clear data, resolution moves faster.
Steady light is not a luxury. It signals a solid, low-impedance electrical path from the transformer to the filament or the LED driver. Achieving that in Houston means accounting for heat, humidity, storms, and the way modern homes stack electronics on existing infrastructure. The process starts with listening and careful observation, then moves through targeted testing and well-chosen repairs: tightening neutrals, correcting splices, upgrading dimmers, balancing panels, and, when needed, coordinating with the utility. The result feels immediate. The chandelier holds steady. The kitchen pendants glide smoothly from bright to a soft glow. The AC can start without a whole-house sigh.
If you are weighing whether to make the call, watch for these signs: lights that flicker on both sides of the house without a clear trigger, outlets or breakers that feel warm, buzzing at the panel, or electronics that reboot when appliances start. Those point to issues that panel buzzing or humming deserve professional attention. A good team that handles electrical repair Houston wide will separate fixture-level nuisances from service-level risks and solve the right problem. Good electrical repair services do not stop at a switch swap. They trace paths, tighten the silent weak links, and leave a system that behaves itself through August heat, September storms, and December holidays.
Home electrical repair should feel practical, not mysterious. Replace the parts that fail, reinforce the parts that age, and design with the loads you actually use. When a home lights the way it should, everything else gets easier, from cooking dinner to reading a bedtime story without the lamp flickering in the corner of your eye. If the lights in your place still waver, give a pro a detailed description and a few data points. The fix is usually closer, and simpler, than it looks at first glance.
All American Electric LLC
Address: 9230 Keough Rd #100, Houston, TX 77040
Phone: (713) 999-3531